High Pressure on Baxi Duo Tec 28 combi boiler, but only when heating is on
11 Jan 2006
I have a Baxi Duo Tec 28 combi boiler. Never had a single issue with it but I noticed yesterday when the heating was on, running at around 67 deg C that the pressure gauge was reading just over 3 bar (See the photo). It usually rises slightly when my heating is on, but not to that sort of pressure.
I switched the heating off and let the system cool down and the pressure gauge returned to its normal reading of around 1.3 bar.
I turned the hot tap on and run it for a few minutes until the hot water reached temperature and the pressure gauge reading remained at around 1.3 bar.
I turned the heating back on and when it reached around 67 deg C, I checked the pressure gauge and again, it was reading just over 3 bar. I turned the temperature down on the boiler to around 50 deg C and after around 15 minutes, I checked the pressure gauge again which was reading about 2.5 bar (the gauge was on the line between the green and the red zone on the pressure gauge.
Can anyone shed any light on what is causing the above to happen and if it's something that I can resolve myself?
Thanks in advance for any responses received.
+1, get the boiler serviced by a GSR engineer asap. Part of that will be to check the expansion vessel, especially given it's current behaviour.
The Pressure Relief Valve will also need checked now, given it should have opened at that pressure and depending on the boilers age, it may even need replaced.
Not really
Your expansion vessel has lost its charge or the internal diaphragm has split mate. When cold it looks fine, but the second the central heating heats up, expanding water has nowhere to go so pressure shoots straight over 3 bar and dumps out the PRV copper pipe outside. You need to isolate the boiler, drain the boiler pressure down with the drain off left open, and check the Schrader valve on the vessel with a tyre pressure gauge. If water squirts out the valve, vessel is dead and needs replacing.