Hive Install on Main 24 HE Combi Boiler

Discussion in 'Plumbing and Central Heating' started by hgrdkx, 7 Jan 2019.

  1. hgrdkx

    hgrdkx

    Joined:
    7 Mar 2018
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi All,

    I'm looking to install a Hive Thermostat, 1 channel reciever onto a Main 24 HE Combi Boiler.

    Looking a bit of advice on how to connect up? I've installed a Hive on my previous boiler which had an external timer connected so that was an easy switch over. This has an internal timer connected into the boiler and just want to double check I'm in the right place before messing about with it.

    Boiler Manual is below:
    http://www.ultimatehandyman.org/PDF/Baxi2/Baxi-Main-Combi-24-HE-Installation-manual-47-474-02.pdf

    Looks like this at the internal timer connection on the boiler (see pictures below) would I be right in thinking I would wire it up like the following?

    BOILER - HIVE
    BR: (Brown): Perm Live - L on Hive
    B (Blue): Perm Neutral - N on Hive
    BK (Black): Switched Live In - Heating On (3) on Hive
    BK (Black) : Switched Live Out - Heating Off (2) on Hive

    Where does the common go?

    I will probably run flex from the PCB rather than using the wiring at the timer connection as from memory the receiver will be too big to fit inside the boiler so will need to be mounted externally.

    Any guidance appreciated.

    Many Thanks.

    Main Wiring Timer Dia.jpg IMG_20190107_132421.jpg
    Hive Install.jpg
     
  2. Sponsored Links
  3. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    12,366
    Thanks Received:
    2,697
    Location:
    Daventry
    Country:
    United Kingdom
    Common is your switch Live in. Don't connect anything to terminal 2.
     
    • Thanks Thanks x 1
  4. hgrdkx

    hgrdkx

    Joined:
    7 Mar 2018
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Brilliant, Thanks for the speedy response!

    To Clarify:

    BOILER - HIVE
    BR: (Brown): Perm Live - L on Hive
    B (Blue): Perm Neutral - N on Hive
    BK (Black): Switched Live In - Common on Hive
    BK (Black) : Switched Live Out - Heating On (3) on Hive

    Would you happen to know a preferred place to mount the receiver? Will 1mm 5 core flex be OK extend wiring to new receiver position?
     
  5. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    12,366
    Thanks Received:
    2,697
    Location:
    Daventry
    Country:
    United Kingdom
    1.5mm is recommended. Not sure how big the Hive receiver is, because I don't fit Hive due to it being ****, but a Nest receiver will fit inside a Main Eco quite comfortably, just above the diverter valve. Other than that, immediately below/beside the boiler is as good a place as any. You need 1.5mm flex
     
    • Thanks Thanks x 1
  6. Sponsored Links
  7. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    18,593
    Thanks Received:
    7,287
    Location:
    Lanarkshire
    Country:
    United Kingdom
    Sorry but both nest and hive receivers should be 300mm away from the boiler or any additional electrical appliances fridges etc this si to stop signal interference between the thermostat and the receiver
     
    • Like Like x 1
  8. Gadget Goblin

    Gadget Goblin

    Joined:
    4 Oct 2019
    Messages:
    1
    Thanks Received:
    0
    Country:
    United Kingdom

    Hi there, I have the same current set up as you and was wondering which black wire is which

    here’s a pic of mine
     

    Attached Files:

    Last edited by a moderator: 4 Oct 2019
  9. sp

    sp

    Joined:
    6 Jun 2004
    Messages:
    25
    Thanks Received:
    0
    Country:
    United Kingdom
    Gadget Goblin,
    Don't touch the timer wiring ,just keep it on constant
    or if you have connector block as shown in picture , disconnect timer wiring and connect black wires in same block, brown and blue separately ( check picture 1)

    For single channel Hive
    boiler live to hive live
    boiler N to hive N
    boiler E to hive E
    boiler 1 to hive 1(common)
    boiler 2 to hive 3 ( heating on -NO)
    remove link from boiler 1 and 2 terminal
    Check picture 2 1.jpg 2.jpg
     
  10. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    13,467
    Thanks Received:
    2,899
    Location:
    Glasgow
    Country:
    United Kingdom
    If you are looking for an answer to such a simple, Elementary, staring in your face question, leave the task to someone who is good with Lego blocks
     
  11. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page