hob & oven install
18 Jun 2011
Yorkshire
Hi guys,
need some advice i want to fit a hob rated at 6.3kw, & oven rated at 3.2kw.The existing circuit is wired in 6mm fed by 32amp mcb
would i need to have another circuit installed for the oven or could i combine both circuits & fit a 40amp mcb
The 6mm is run through the loft(insulation)
skeets
On the contrary - because of the insulation, but depending on exactly how it is installed, it would be better to fit a 25A mcb.
If you can't find one for your consumer unit then remove the cable from the insulation or vice versa.
This is a previous diagram but apart from the 32A mcb it will do for you.
Fit a 13A fuse in the FCU.
If you do change to a 25A mcb you need not fit the FCU.
Connect both hob and oven cable to a double Connection Unit.
If the cable is laid on the ceiling and covered by less than 100mm. of insulation you can leave the 32A mcb in place.
Edit - In fact a 20A mcb would suffice.