Hi all,
After a bit of help, this is not my area! Came home today to found the house was cold. After some testing found it was the Honeywell v4073a Motorised Valve. (3 pot)
Was going to replace it, but after some testing not 100% sure its at fault, or suspect its gone in a strange way.
First made sure there is no call for HW or CH. I placed the valve in manual override. Pushing the leave I feel a nice level of resistance and can hear the motor turn as I push.
Then made a call for HW - I hear the value move back and the boiler click on. (there is resistance if I try move the leave back to override indicating it moved.)
Next I kill the call for water...
I make a call CH - There is no movement on the valve, the boiler remains off.
If I manually push the leaver to override, the boiler clicks and the heating comes on.. The heating operates normally with the rooms stat.
If then there is then a call for HW nothing changes. (HW+CH), I hear nothing form the valve.
When the CH ends, and the HW call is still active the valve move as mentioned above..
Its like the valve has 50% failed, e.g. it can move from CH to HW, but cant move back.. Is that possible?
I'm pretty sure its the value as I can get all bits of the system to work just by having the value in the various position.
Should I replace the powerheard or the complete valve?
Or I have I missed something..
Many thnaks
After a bit of help, this is not my area! Came home today to found the house was cold. After some testing found it was the Honeywell v4073a Motorised Valve. (3 pot)
Was going to replace it, but after some testing not 100% sure its at fault, or suspect its gone in a strange way.
First made sure there is no call for HW or CH. I placed the valve in manual override. Pushing the leave I feel a nice level of resistance and can hear the motor turn as I push.
Then made a call for HW - I hear the value move back and the boiler click on. (there is resistance if I try move the leave back to override indicating it moved.)
Next I kill the call for water...
I make a call CH - There is no movement on the valve, the boiler remains off.
If I manually push the leaver to override, the boiler clicks and the heating comes on.. The heating operates normally with the rooms stat.
If then there is then a call for HW nothing changes. (HW+CH), I hear nothing form the valve.
When the CH ends, and the HW call is still active the valve move as mentioned above..
Its like the valve has 50% failed, e.g. it can move from CH to HW, but cant move back.. Is that possible?
I'm pretty sure its the value as I can get all bits of the system to work just by having the value in the various position.
Should I replace the powerheard or the complete valve?
Or I have I missed something..
Many thnaks