Dear all,
In my parents house, they have a vented system, when they turn the HW on the rad in the bathroom gets hot (the ch is not on at this point), I thought it might be the three port valve, but have changed that and it still happens, would this be a plumbing problem or does it sound like the electrical controls have been misconnected.

Thanks in advance

Vic
 
It sounds as if it may have been plumbed into the HW heating cuitcuit.

Some installers thought that was better!

Tony
 
It is done so that towels can get dried on a rad during periods when CH is not being used (e.g. summer).
 