Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.
Have a fully pumped system with a three port valve. Rads getting hot when hot water only is selected. Have already changed three port valve. Please help - getting desperate !
Complete valve was changed this week. Fault occured overnight approximately one month ago - working fine until that point. System approximately 15-20 years old in microbore. Boiler is fan assisted. Anything else you need to know ?
DO check the pump is pumping towards the middle connection. They work to varying extents backwards, but always end up "letting by". Could have always been wrong.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local