Ideal minimser dry fire thermostat

Joined
1 Feb 2010
Messages
3
Reaction score
0
Location
Cumbria
Country
United Kingdom
Why does the dry fire thermostat keep tripping the boiler.sometimes after about an hour, other times after about ten minutes?
 
Why does the dry fire thermostat keep tripping the boiler.sometimes after about an hour, other times after about ten minutes?

Not the overheat stat. The dry fire thermostat is wired in series with the pressure switch and the flue thermostat.(in Manual) I can't see where the capillary from the stat goes.
Thanks
 
I cant picture it. Usually see response's rather than minimisers.

Is it definately the dry fire stat causing issue?
 
ive only ever had these go repeatedly when the heatex is buggered. theres plenty of ideal guys on here, im sure they could shed more light.
 