i have the expansion pipe tee,d off the flow at the cylinder and i have the cold feed connected into the expansion pipe,
The
vent pipe should rise to the cold feed & expansion tank.
The
cold feed should be connected on the return side of the cooling set up, whether that is a hot water cylinder, thermal store, radiator, cooling coil, plate cooler or some other method.
So in an over heat situation a safe circuit is acheived keeping the boiler cooled.
Your first priority is to ensure the gravity circuit is thermo syphoning without any pumps operating. Thats quite easy to do by just feeling the pipes.
What size pipes have you used? Have you ensured a rising gradient on the flow and a falling gradient on the return?
Have you used a pipe bender to make direction changes?
Up too 6m horizontal with a 0.8% gradient will work with 28mm pipes!
Will your pipework configuration allow air to escape without pockets?
A hi-Lo stat set up should be used.
If you only fit a flow stat, cold water from the heating circuit will be dumped back into boiler return creating condensation and cold flue problems leading to early boiler failure and will also cool the hot water in the cylinder!
i wonder would the pressure of the cold feed prevent the clyinder flow from circulating
No