Joining 8 T&E Cables

Joined
14 Dec 2010
Messages
197
Reaction score
11
Location
Birmingham
Country
United Kingdom
Hi,

I'm installing a couple of new lighting circuits and need to join 8 (or so) feeds to a single T&E for going into my CU.

The longer term plan is to have a central bank of dimmers near the CU and I'll replace this 'thing' with an 8 channel intelligent dimmer - hence why I need to bring the individual light cables back and can't just branch off the previous light in the circuit.

In the meantime though I just want to get it in so I can upgrade at a later date.

I realise I could just daisy chain junction boxes but thought there may be a better method?

Cheers,
 
Sponsored Links
Presuming they are 1.0 or 1,5mm cables then a double surface pattrass with blanking plate will do with connector blocks inside as long as its accessable and the cables can be clipped upon entry.
 
R426171-11.jpg
 
Sponsored Links
Personally i'd just use an ordinary strip of terminal block inside a suitable enclosure. On one side I would have the cables to the lights with two wires per hole (so 12 holes total). On the other side I would have the incoming cable and link wires.
 
what dimmer are you going to use? looking recently there are a few that are DIN mounted, so Id go with a box with a DIN rail in it and some DIN mounted connector blocks (as BAS' pic)
 