I HAVE A SIME FORMAT 30HE COMBI BOILER AND IT HAS LOST PRESSURE(ZERO) THE HEATING IS WORKING FINE BUT I AM STRUGGLING TO GET HOT WATER.ANY SUGGESTIONS? REGARDS MIKE[/b]
 
EVER THOUGHT OF READING THE FAQ?
GET YOUR CAPS LOCK REPAIRED WHILST YOU ARE AT IT.
 
Open both valves on the filling loop (pictured above) Then keep an eye on the pressure dial.

When it reaches 1.5 bar shut the valves.

Job done :wink:

Then keep an eye on the pressure over the next few days to make sure you don't have a leak :)
 
Job sorted many thanks.
Open both valves on the filling loop (pictured above) Then keep an eye on the pressure dial.

When it reaches 1.5 bar shut the valves.

Job done :wink:

Then keep an eye on the pressure over the next few days to make sure you don't have a leak :)
 