• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

MAIN combi 24 HE

Joined
23 Dec 2010
Messages
3
Reaction score
0
Location
Manchester
Country
United Kingdom
condensation pipes had frozen this morning and backed up into the boiler trap, Ive successfully defrosted and drained all the water. The problem now is the FLAME failure light is permanently lit, no noise or anything happening :cry:
 
A contact at the top of the condensate pipe checks that the trap is not full.

Either yours still is or its just still wet on the surface.

Tony
 
ive fully drained the trap and now disconnected the 2 teminals, both dry but gonna leave them off for a bit to make sure. See how that goes
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top