main Earth wire

  • Thread starter Thread starter llewop
  • Start date Start date
L

llewop

Can some one confirm to me that it is a 10mm earth cable you use to bond the main gas and water pipes at the consumer unit. Also is it a 10mm cable you take from the cable head as you main earth into the consumer unit.
 
I think it`s pme. It has a seperate earth block next to the cable head with the mains earth going in to it
 
10mm² to water/gas (altho some DNO's prefer 16)

16mm² from supply to MET/CU
 
You need to contact your DNO (distribution network operator) to find out what size main equipotential bonding (water + gas) needs to be installed.
 