maximum curent carrying capacity for....

Joined
27 Aug 2011
Messages
18
Reaction score
0
Location
Lancashire
Country
United Kingdom
whats the maximum current carrying capacity for 2.5 sq mm copper wire and also 6 sq mm copper wire?

cheers
 
Sponsored Links
What type of 2.5 and 6.0mm² ?

How is it installed ?

How far ?

What ambient temperature ?

What is the protective device ?
 
The type of wire is multi stranded for both 2.5 and 6.0 sq mm

it is installed through conduit

the length is about a meter

The temperature is room temperature

the protective devices are a mcb and also rcd
 
Sponsored Links
whats the maximum current carrying capacity for 2.5 sq mm copper wire
for single phase:
T&E 27A
Multicore 27A
Singles 27A

and also 6 sq mm copper wire?
T&E 47A
Multicore 46A
Singles 47A

These are the Maximum current carrying capacity.
You will need to take in to consideration the reference method, length and protective device type protecting the circuit, when designing the circuit as these could factor in a de-rating of the cables capacity.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back