maximum curent carrying capacity for....

What type of 2.5 and 6.0mm² ?

How is it installed ?

How far ?

What ambient temperature ?

What is the protective device ?
 
The type of wire is multi stranded for both 2.5 and 6.0 sq mm

it is installed through conduit

the length is about a meter

The temperature is room temperature

the protective devices are a mcb and also rcd
 
whats the maximum current carrying capacity for 2.5 sq mm copper wire
for single phase:
T&E 27A
Multicore 27A
Singles 27A

and also 6 sq mm copper wire?
T&E 47A
Multicore 46A
Singles 47A

These are the Maximum current carrying capacity.
You will need to take in to consideration the reference method, length and protective device type protecting the circuit, when designing the circuit as these could factor in a de-rating of the cables capacity.
 