MCB rating for 3ph Ind Microwave...?

J

Jagermini

Hey folks, just wondering does anyone out there know size MCB there should be for a 3-phase Industrial microwave, 9000W? Cable run is just 15 meters...
I've worked it out to be load of about 14A, so it should be really a 20 A MCB. That sound right?
 
Sponsored Links
Cheers, been a while since I had to work it out myself, just making sure the maths wasn't rusty. Yeah, I've got 6sq SWA sitting there, 5 core, so the rest should be no bother at all. Sound!
 
Sponsored Links
I was mis-informed, 'tis a 12kW frier. I think it still stands.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top