Can anybody explain to me how I get the radiator output in btu, from the room heat requirement in btu, using the Mear's calculator, on the instruction manual page 5 it shows a temperature difference of 108f , I did try using their example's page 8 just could not get same figure. some assistance truly welcolme.

Thanks
 
Sponsored Links
No only do they work in outdated units that we dont use now but they are usually seriously over sized ( like 20% ).

I would always recommend the whole house method which seems more accurate.

Tony
 
I expect he is quoting a Mear's booklet and that refers to the differential between mean rad temp and the room.

Tony
 
Sponsored Links
I expect he is quoting a Mear's booklet and that refers to the differential between mean rad temp and the room.
If, so that's a very low differential. Rads specs are based on a 50°C differential. A 1kw rad (75/65/20) will reduce in output to 800w (67/57/20). So you would have to install a 1250W rad to give the 1000w actually wanted. This would explain the 20%+ oversizing that you mentioned earlier.
 