I agree that the regs don't explicitly say that it doesn't apply to bonding conductors, but the spirit of the regs maybe implies that.The regulations don't say they don't.do the requirements for cables to be in safe zones (or otherwise protected) actually extend to bonding cables?
In particular, 522.6.101(i) allows a cable to be buried <50mm deep if it has an 'earthed metallic covering'. If the entire (and only) conductor is already earthed (at least as well as any covering would be), such a covering would obviously achieve nothing - and suggest to me that the regs don't really intend the 'buried cable rules' to apply to cables which contain only bonding/earthing conductors.
Kind Regards, John