Multiple loads on a Radial
15 Nov 2005
South
Cook Islands
This is a small change to a final circuit, not in a bathroom or kitchen so I am doing it in my capacity as sensible householder.
An elderly relation has a modern CU with MCBs under the stairs, neatly and professionally installed. It includes a 20A radial marked "this cupboard" which just supplies a double switched socket close to the CU. However my relation has plugged a doorbell transformer into one socket, and an outside lamp in the other. I was planning to put both of these onto FCUs with 3a cartridges and run in 1.5mm T&E.
However, I have only used radials before with a single appliance on them (immersion heater, shower, freezer usw.) I looked in my OSG and browsed the reference section here, couldn't find anything about having multiple loads on a radial. Is it permitted? Is there a particular way to do it (like having a fused spur off a ring?) If I can, I'd like to retain the socket outlets as well, as they're handy for hoovering the hall.
No problem to adding FCU but if these appliances are on fused plugs you cound just add another double switched socket outlet.
There is nothing in the regs against having as little as two doubles off a 20A fused radial, and perfectly safe.
Add the FCUs onto the end of the radial using 2.5mm² T&E (not 1.5mm²)
oh, yes, I see what you mean, keep the radial in 2.5 so it is protected by the 20A MCB. What I had in mind was the cable from the FCU to the load can be 1.5mm (they are currently both in flexible cords from the plugs).
Can a radial have several sockets on it, then? Is there a limit, like the 100 sq m floor area of a ring?
Yeah, you're free to use 1.5mm² on the load side of the FCU
Yes, and 50m² for 16/20A Radials, and FWIW, 75m² for 32A radials