my baxi megaflo 32kw system boiler cycle - is this normal?

Discussion in 'Plumbing and Central Heating' started by andreitone, 28 Nov 2008.

  1. andreitone

    andreitone

    Joined:
    2 Nov 2008
    Messages:
    10
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,

    CH water temperature is set at 55 deg Celsius

    this is how it cycles:

    burner starts at 42 deg, heats the water at 58 deg in 10 seconds, then after 2 minutes the burner stops when the water reaches 60 deg.
    the water temperature drops at 45 deg in about 30 sec, then after about 3 minutes the burner starts at water temperature of 42 deg.

    I don't know exactly what temperature is shown on the display but I think is the return temperature.

    I do think it's cycling too fast burner on/off and when the burner starts the water (return) heats up too quickly, I think it's because of the automatic integral bypass.

    My question is:

    Is this normal functioning?
    Is there a way of adjusting the automatic integral bypass in this type of boiler?

    Thanks
     
  2. Sponsored Links
  3. spudkey

    spudkey

    Joined:
    27 Oct 2007
    Messages:
    819
    Thanks Received:
    223
    Location:
    Essex
    Country:
    United Kingdom
    does it do this from cold, how many rads do you have do you have a room stat
     
  4. andreitone

    andreitone

    Joined:
    2 Nov 2008
    Messages:
    10
    Thanks Received:
    0
    Country:
    United Kingdom
    thanks for the reply.

    It doesn't do this from cold, but in normal cycling. I have 7 radiators and no room stat yet, also no TRV's on the rads.

    The rads are set as to have a 20 deg celsius differential on the return (so if 55 deg on the flow there is 35 deg on the return).
     
  5. spudkey

    spudkey

    Joined:
    27 Oct 2007
    Messages:
    819
    Thanks Received:
    223
    Location:
    Essex
    Country:
    United Kingdom
    32kw is a big boiler for 7 rads how was this boiler sized, if you are trying to get 20c temp drop across rads by balancing lockshield valves then i think the bypass will be opening. Even at lowest modulation this boiler gives 9kw this is enough for many 3 bed houses
     
  6. David937

    David937

    Joined:
    7 Aug 2008
    Messages:
    1,064
    Thanks Received:
    49
    Location:
    Farndon
    Country:
    United Kingdom
    Have you tried a higher flow temperature?
     
  7. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,039
    Thanks Received:
    4,595
    Location:
    London
    Country:
    United Kingdom
    It seems to me that this boiler has been massively oversized!

    For a start you could set the boiler to minimum output power although even that will be far too much!

    Tony
     
  8. Sponsored Links
  9. andreitone

    andreitone

    Joined:
    2 Nov 2008
    Messages:
    10
    Thanks Received:
    0
    Country:
    United Kingdom
    I have tryed 60deg but did not watch it's cycle


    For a start you could set the boiler to minimum output power although even that will be far too much!

    Agile how can I do this?
     
  10. andreitone

    andreitone

    Joined:
    2 Nov 2008
    Messages:
    10
    Thanks Received:
    0
    Country:
    United Kingdom
    thanks for the reply spudkey, would you think that a 10 deg temp drop across rads and lowering the CH water temperature will help the boiler not cicling as much?
     
  11. David937

    David937

    Joined:
    7 Aug 2008
    Messages:
    1,064
    Thanks Received:
    49
    Location:
    Farndon
    Country:
    United Kingdom
    Tony can you set the boiler to minimum rate by adjusting the Min rate adjustment screw?
     
  12. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,039
    Thanks Received:
    4,595
    Location:
    London
    Country:
    United Kingdom
    No, you call the installer and ask him to set it at the minimum output.

    However, as he seems to have fitted a boiler which is totally oversized I would not expect that he can be trusted to do anything. I doubt that he is even CORGI registered.

    Tony
     
  13. andreitone

    andreitone

    Joined:
    2 Nov 2008
    Messages:
    10
    Thanks Received:
    0
    Country:
    United Kingdom
    In my country is very hard to find a professional installer...

    Agile is it very hard to set it at minimum output? I think I saw something on the internet about this but can't find it anymore... I'd like to give it a try
     
  14. David937

    David937

    Joined:
    7 Aug 2008
    Messages:
    1,064
    Thanks Received:
    49
    Location:
    Farndon
    Country:
    United Kingdom
    I not sure the way I described is actually the way to do it. It might not be allowed,AIUI the adjustment screw is only for installers to adjust.
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page