Just moved into a new house last Friday and found that hot water from boiler is not working so have had to use immersion.
Investigating further today and I think the problem lies with the 3 way valve (model as above).
Could someone confirm that I am heading in the right direction please?
I have taken the actuator off the valve and the valve shaft is easily turned by hand so I think that mechanically all is well. The actuator itself is very hot even though the heating has been off all day and the manual/auto lever is just flopping around with no resistance. Can I therefore deduce that the actuator is shot?
I can get hold of and fit a new actuator if someone could confirm that I am on the right lines, but in the meantime is it possible to get the HW to work by manually turning the valve shaft? and if so in which direction? ( or do I just turn it until I get hot water?)
Thanks for any advice.
Investigating further today and I think the problem lies with the 3 way valve (model as above).
Could someone confirm that I am heading in the right direction please?
I have taken the actuator off the valve and the valve shaft is easily turned by hand so I think that mechanically all is well. The actuator itself is very hot even though the heating has been off all day and the manual/auto lever is just flopping around with no resistance. Can I therefore deduce that the actuator is shot?