You need to get a bucket or saucepan of known volume ( can check by filling using a measuring jug. ).
Then time how many seconds it takes to fill this container. Measure at kitchen cold tap and then at bath cold tap and then at bath hot tap.
Thanks for that Tony - have done so & here's the results:
1ltr jug
Cold Kitchen Tap: 6.5s
Hot Kitchen Tap: 9.5s
Cold Bath Tap: 5.5s
Hot Bath Tap: 9.5s
(also did cold & hot bathroom sink taps which were exactly the same as the bath)
We have concluded that our hot water pressure in the kitchen only appears so vastly improved cos it literally used to trickle taking an eternity to fill the sink for washing up!
Anyway, these figures work out that we're getting approx. 9ltrs/min of cold water from the mains & 6ltrs/min of hot water from the boiler - nowhere near the 9ltrs specified by another member on this thread.
Am I right in deducing that its more than likely the pipe coming off the mains, up our drive & into the property? Or is there a setting on the boiler to increase the hot water pressure?
I'd like to add that its been in the 20's heat wise for a couple of weeks now so surely there's no reason why the boiler should've "slowed down" to that?
There are no settings on the Junior, as it is Worcesters' entry level boiler, however, being a combi, running on mains pressure, the flow rates of hot and water should be pretty much the same. The boilers' resistance to the hot water flow should be minute and it should give 11.5 liter per minute on 30 cell degrees rise.
I would check that the cold water inlet gate valve to the boiler and / or any other valve on the hot water side (if you have one) are fully open.
If non of this work call an engineer to clean the filter, Flow Restrictor housing, or replace the Flow Restrictor.
good luck.