Good morning/evening
Ive just recently moved into a new (old) house and having a problem with the CH & HW...
our system which i suspect is on a W plan is:
The previous owners would use the main switch on the boiler to turn the system off and on as theres no CH programmer to be found in the house which i found bizarre.
Today theres been no HW but the CH has worked fine when the boilers been on so i went to check the immersion heater and the 3 port valve seemed to be stuck halfway, with the little lever moving freely without resistance, when i took the actuator off it would click every second or so and the valve spindle moves freely around 10/15 degrees left and right. Im guessing ill need to replace the actuator as the lever isn't working and its a honeywell model that allows me to without draining. i found the immersion stat under the floor boards which was set to 90 degrees which i imagine is way to high so lowered down to 55.
But heres the wiring, and for some reason im thinking this is wrong and needs redoing... would i be correct? ive also done some research and although the 3 port valve says Y plan i was thinking that i have a W plan so was wondering if you think its worth changing if thats the case?
If anyone could offer help id greatly appreciate it.
Cheers
Ive just recently moved into a new (old) house and having a problem with the CH & HW...
our system which i suspect is on a W plan is:
- Glow worm compact boiler - discontinued - no programmer fitted
- 900x450 Immersion heater
- Honeywell sundial Y plan V4073A1039
The previous owners would use the main switch on the boiler to turn the system off and on as theres no CH programmer to be found in the house which i found bizarre.
Today theres been no HW but the CH has worked fine when the boilers been on so i went to check the immersion heater and the 3 port valve seemed to be stuck halfway, with the little lever moving freely without resistance, when i took the actuator off it would click every second or so and the valve spindle moves freely around 10/15 degrees left and right. Im guessing ill need to replace the actuator as the lever isn't working and its a honeywell model that allows me to without draining. i found the immersion stat under the floor boards which was set to 90 degrees which i imagine is way to high so lowered down to 55.
But heres the wiring, and for some reason im thinking this is wrong and needs redoing... would i be correct? ive also done some research and although the 3 port valve says Y plan i was thinking that i have a W plan so was wondering if you think its worth changing if thats the case?
If anyone could offer help id greatly appreciate it.