The basic standard for cylinders now requires a certain minimum tramsfer rate.
Your boiler is probably correctly matched for the house at about 10-12 kW and that would be about right for a standard cylinder.
The transfer rate is only when nthe cylinder water is cold and is less when its already warm.
In any case 12 kW will only heat about 5 li/min so you cannot rely on that to reheat the cylinder.
I can see no reason to pay more for a high output cylinder in your situation. Merely sizing it correctly will provide you with what you need.
You can see the power input of your boiler by measuring the gas comsumption at the meter and see in the FAQ how to do it. Then multiply by about 0.7 to get the actual heat output.
Tony
Your boiler is probably correctly matched for the house at about 10-12 kW and that would be about right for a standard cylinder.
The transfer rate is only when nthe cylinder water is cold and is less when its already warm.
In any case 12 kW will only heat about 5 li/min so you cannot rely on that to reheat the cylinder.
I can see no reason to pay more for a high output cylinder in your situation. Merely sizing it correctly will provide you with what you need.
You can see the power input of your boiler by measuring the gas comsumption at the meter and see in the FAQ how to do it. Then multiply by about 0.7 to get the actual heat output.
Tony