no heat or hot water

Joined
16 Feb 2007
Messages
12
Reaction score
0
Country
United Kingdom
Hi

this is an old house with some modernisation to the CH system. The boiler (about 4 years old) is Halstead Best db 80. The system is open, part pumped, part gravity.

After fitting a new rad, the boiler strikes up when cold. The pump seems to be working and circulating water through rads... but the circulated water is cold and there is no hot water going to tank. feed from boiler to pump is getting very hot, not much going on from pump onwards. consequently, the boiler sits idle, I suppose 'thinking' the temp of the system is at optimum.

please could anyone advise what the problem might be, where to start looking? I have called an engineer, but am waiting for call back

many thanks
 
Either the pump is not working. See FAQ for checks.

Or there is an airlock. See if any manual bleed points anywhere. Did you bleed the pump?? See FAQs

Would be a good idea the get the system properly controled with a pumped HW system.

Tony
 
thanks Tony... turned out the pump was on its last legs... now replaced and seems to be working fine...

Simon
 