noisy Grundfos on secondary flow

Min

Joined
27 Oct 2003
Messages
291
Reaction score
7
Country
United Kingdom
We have had secondary flow plumbed in with a Grundfos pump (so that there's hot water instantly at the taps, don't have to run off cold water first).

When it's been on for a while (maybe half an hour) the pump starts screaming. The plumber returned and bled the pump, then replaced the non-return valve with an ordinary cut off valve but the pump stills screams.

Any ideas?

Thanks

Mary
 
Sponsored Links
Yes, you're running the pump dry.

Either an air lock or bad installation.

A photo of the pump and local pipework please.
 
fistly for a secondary return to prevent dead legs the pmp should be on the return (close to the h/w cylinder)! and also it should really be a pump with green casing (a bronze impellor-to prevent corrosion).
 
fistly for a secondary return to prevent dead legs the pmp should be on the return (close to the h/w cylinder)! and also it should really be a pump with green casing (a bronze impellor-to prevent corrosion).

thats a WILO, grundfos are yellow :LOL:
 
Sponsored Links
fistly for a secondary return to prevent dead legs the pmp should be on the return (close to the h/w cylinder)! and also it should really be a pump with green casing (a bronze impellor-to prevent corrosion).

Firstly, every outlet teed off an secondary circuit will be a dead leg, the circuit simply reduces the length of the leg.

Secondly, the pump can be installed in the flow or return, although it's more common fitted in the return.
 
We have had secondary flow plumbed in with a Grundfos pump (so that there's hot water instantly at the taps, don't have to run off cold water first).

When it's been on for a while (maybe half an hour) the pump starts screaming. The plumber returned and bled the pump, then replaced the non-return valve with an ordinary cut off valve but the pump stills
Sounds as if the pump is running all the time with insufficient flow. With pump running and pumping hot water cavitation will probably occur in the pump which will then mean it is then running dry, pumping air.

Pump needs to be fitted with a thermostat so that it only runs to keep the secondary circuit hot.
 
Thanks guys.

Yes, it is a bronze impellor.

Pump fitted in flow. Plumber says he has fitted lots like this and it hasn't been a problem, but is willing to come back and change it to the return.

I'll also ask him about fitting a thermostat so the pump isn't running all the time when it's on.
 
When it's been on for a while (maybe half an hour) the pump starts screaming. The plumber returned and bled the pump, then replaced the non-return valve with an ordinary cut off valve but the pump stills screams.

Any ideas?

Thanks

Mary

Possibly cavitation, which is nothing to do with it sucking air in.

It has much to do with the temperature of the water and the pressure available at the pump inlet.

There are energy losses due to friction in the pipes and in every fitting; the energy lost is provided by a pressure loss as the fluid progresses along the circuit. There are high eddy velocities in the pump inlet and these also cause a reduction in fluid pressure.

If the pressure drops low enough and the water temperature is high enough, then the water will boil in the pump inlet. Bubbles of vapour form and these implode as they progress into the pump's discharge.

There is a distinctive sound, like gravel. It will tear lumps of bronze out of the pump's impeller.

The cure is to reduce temperature, increase static pressure and/or reduce frictional pressure losses on the inlet pipework. It more likely if there's little head between pump and the water level in the cold feed storage cistern (assuming it's a vented system).

The pump's usually fitted in the return because the water's cooler. You can also get bubbles of dissolved oxygen coming out of solution, due to the low pressures in the pump inlet, as described by someone above; this isn't cavitation, but it can cause the pump to airlock. A shower pump, for example, will take the water flow from an Essex/Warix/Surrey or similar flange, which is designed so that it doesn't collect the air bubbles from the cylinder.

Ask the plumber whether he thinks it may be cavitation; watch for the blank expression as you do so.
 