Hi Tony, if you are still there.
On the boiler terminal, with the live wire to the pump removed there is no output voltage between the pump live terminal and the earth when the boiler is fired up, so I think this confirms your diagnosis that there is a problem with the boiler, probably the pcb.
What still confuses me is the voltage betwen the live pump wire to the boiler (bare wire) and the earth is still 108V. The 108V is always on when the programmer is set to either CH or HW or both are on. The voltage goes off when the CH and HW are off. I think the pump must be wired to the programmer as well as diirectly to the the boiler, would that be normal? and if so would the 108V be normal?
Th CH system has worked fine since the new boiler was put in 5 years ago and still works fine with the pump running independantly but continuously from a 13 amp socket. I haven't changed any of the wiring.
On the boiler terminal, with the live wire to the pump removed there is no output voltage between the pump live terminal and the earth when the boiler is fired up, so I think this confirms your diagnosis that there is a problem with the boiler, probably the pcb.
What still confuses me is the voltage betwen the live pump wire to the boiler (bare wire) and the earth is still 108V. The 108V is always on when the programmer is set to either CH or HW or both are on. The voltage goes off when the CH and HW are off. I think the pump must be wired to the programmer as well as diirectly to the the boiler, would that be normal? and if so would the 108V be normal?
Th CH system has worked fine since the new boiler was put in 5 years ago and still works fine with the pump running independantly but continuously from a 13 amp socket. I haven't changed any of the wiring.