. The water level in the F/E tank isn't exactly high as it is, only a couple of inches over the fill pipe, and the Vent pipework already goes all the way to the rafters, so no additional height available there either

I was suggesting to increase the diameter of 22mm OSV above the water line ie: a short piece of 42mm , this will normally cure any surge issues due to the increased volume of pipework , or maybe fit an air separator?
 
Sponsored Links
Have you bled all the rads?

Then cut out the tee where the vent is connected and check for blockage...a magnet won't always find a restriction.
 
Your mock-up is exactly how it should be done, make sure the vent and cold feed are not more than 150mm apart.
 