Can anyone help me determine the size of the flex cable I need to install on a Siemens oven?

It's rated at 4.9kW and the manual states it needs to be wired using a type H05 VV-F or higher.

Thanks

Howie
 
Sponsored Links
Sponsored Links
thanks, the circuit is protected by a 32A MCB. Also on this circuit will be a hob and the socket outlet.
 
The main thing to consider here is the load, as even a B50 breaker will only need a 1mm cpc for fault protection under ADS.
 