Ceramic Hob Cable

Joined
7 Mar 2003
Messages
49
Reaction score
0
Country
United Kingdom
Hello

I'm about to install a ceramic Hob which doesn't come with a power lead. The instructions recommend "Power Cord Type H05 VV-F or higher" this means nothing to me!

Andy
 
Sponsored Links
Andy Velcro said:
Hello

I'm about to install a ceramic Hob which doesn't come with a power lead. The instructions recommend "Power Cord Type H05 VV-F or higher" this means nothing to me!

Andy
H- harmonised
05 - 300/500V
VV - PVC PVC
F - fine wire flex

tell us the power rating and well be able to tell you what CSA youll need. itll prob need 2.5, possibly 4
 
Thanks for the reply. I've had a look and the only figure relating to power is 6600w which I presume is 6.6Kw, is that any help.

Andy
 
Andy Velcro said:
Thanks for the reply. I've had a look and the only figure relating to power is 6600w which I presume is 6.6Kw, is that any help.

Andy

28A. would need 4mm at least. altho, most people would just wire them with 6 or 10mm T+E. what size is the existing cable and MCB/fuse?
 
Sponsored Links
i would reommend using 6mm T+E to connect it.
 
Andy Velcro said:
The instructions recommend "Power Cord Type H05 VV-F or higher" this means nothing to me!
It would have done if you'd bothered to look in the For Reference section...
 