Performa 28 hw works ch kicks in but does not circulate plz

Joined
1 Dec 2010
Messages
2
Reaction score
0
Location
Bath
Country
United Kingdom
Hello,

I have a Potterton Performa 28.
The hot water works perfectly. The problem I have is with the central heating, it does not circulate the heated water. When I switch the CH on the temp increases to 80 degrees in about 20 seconds and then cuts the boiler out for a couple of mins, it then restarts with the same problem.


The CH flow pipe heats up but it seems the return is not working.

I checked the pump via the vent screw with a screwdriver and stopped the pump without much force. I have replaced the pump with a new one but still have the same problem.

Could it be the PCB?

Can anyone please shed some light.
 
Sponsored Links
The return filter is probably blocked its on the return iso valve.3/4" with 1/2" blank or your filling loop on the end.
 
Sponsored Links
Thank you all

The problem was the return valve filter completely blocked :)

Thanks again
 