• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Pipestat help

Joined
22 Dec 2012
Messages
10
Reaction score
0
Location
West Midlands
Country
United Kingdom
I have a Honeywell L641B pipestat which I am looking to connect to an existing Honeywell Froststat in the garage to tighten down in the energy bills.

I have read the forums and was expecting only 2 terminals to be used (1 and 3). I was prepared for L in 1 out on 3 into pipestat 1 and out on C to terminal box. From the photo you can see terminal '2' is used... What is this for?

Also can I run the cable behind the outlet pipe in 25mm plastic trunking to the inpet pipe (on the right)?

Thanks View media item 58986 View media item 58987
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top