Pipestat help

Joined
22 Dec 2012
Messages
10
Reaction score
0
Location
West Midlands
Country
United Kingdom
I have a Honeywell L641B pipestat which I am looking to connect to an existing Honeywell Froststat in the garage to tighten down in the energy bills.

I have read the forums and was expecting only 2 terminals to be used (1 and 3). I was prepared for L in 1 out on 3 into pipestat 1 and out on C to terminal box. From the photo you can see terminal '2' is used... What is this for?

Also can I run the cable behind the outlet pipe in 25mm plastic trunking to the inpet pipe (on the right)?

Thanks View media item 58986 View media item 58987
 
Sponsored Links
Sponsored Links
it 2 is the neutral it should not be connected when used as a frost stat
 