Planning Q

Joined
10 Dec 2008
Messages
975
Reaction score
18
Location
Jersey Marine
Country
United Kingdom
For a new build … I will request a 3ph supply.
3ph is only required in the garage for some machines & a Solar inverter.

Can/should you use use more than 1ph throughout the house to maintain balance …. I could use 1 for single ph power in garage, 1 for downstairs & 1 for upstairs.
Or is there too much risk mixing the phases.

This is only for me to start thinking about distribution layout.
 
Phase balance is mostly irrelevant for the loads found in a domestic dwelling.

However with a solar inverter you presumably want to actually use a majority of the energy being created, and if you only connect a single phase to the property loads you will only be able to use about a third of the available generated energy. The rest will be exported or wasted.

. I could use 1 for single ph power in garage, 1 for downstairs & 1 for upstairs.
You could, but that's a very poor choice. It will put all of the large kitchen/cooking loads on a single phase, and assuming your 'upstairs' is the usual bedrooms and so on that will have next to nothing on it,.
If you want 3 phase and the benefits from that 3p solar inverter, then you wire the property so that the phases are distributed across the whole property, not segmented into large areas.
 
However with a solar inverter you presumably want to actually use a majority of the energy being created, and if you only connect a single phase to the property loads you will only be able to use about a third of the available generated energy. The rest will be exported or wasted.

Thanks for the comments on balance.
Will consider kitchen on 1 ph, cooker on its own feed on another ….


On generation, not quite the case on my use.

Any excess would be stored in on-site batteries (similar to 20kWh storage I have in my current place).
A 3ph inverter allows me to have a DC EV charger of 25KW, thereby allowing Fast charging at home, and if I want it, the option to run house off the car battery if required (V2X once ratified). … in a ‘Grid Outage’ though my batteries more likely to be used.
 
Last edited: