Hi Guys,

Potterton flamingo 20-30 is fine on H/W but appears to be overheating when on C/H. After about 45mins of C/H boiler shuts itself down and pilot light would go off. I have to press the reset button to re-ignite pilot light and would fire up again without any problems. Since it happens only on C/H my first thought was may be there is blockage in C/H but i've checked all Radiators and appears to be warming up ok. Any help would be appreciated.

Thanks in advance!
 
Sponsored Links
Sounds like a failed/failing pump.

See the FAQ on checking your pump.

Tony
 
Sponsored Links
Tony, why failed pump? With dicky pump, surely circulation to gravity HW (I am assuming this is what is in place) would not O/H boiler. If fully pumped CH+ HW, failed pump would O/H boiler during HW demand. Or am I talking rubbish
 
san04, you don't say how your system is configured, ie fully pumped using a motorised valve, or pumped heating with gravity circulation to the cylinder. If the latter there will be 2 x 28mm pipes plus the heating circuit connected to your boiler.
 
it has Drayton motorised valve and there is a pump to one of the , think its fully pumped using a motorised valve ??
 
it has Drayton motorised valve and there is a pump to one of the pipe*, think its fully pumped using a motorised valve ??
 
Post a pic of the pipe connections to the boiler and the pipes and valves in the airing cupboard.
 
Tony, why failed pump? With dicky pump, surely circulation to gravity HW (I am assuming this is what is in place) would not O/H boiler. If fully pumped CH+ HW, failed pump would O/H boiler during HW demand. Or am I talking rubbish

We dont know how the system is configured ( yet ).

I dont assume what the HW is. Even gravity often has a Drayton or Clytrol non electrical control.

If it was fully pumped and the pump failed then if the HW circuit was open that will often create enough gravity circulation to prevent the boiler from overheating.

I still expect its a pump problem but it could also just be sludge blockages.

These are crosswords without clues!

Tony
 
OP, is the motorised vave 2 port or does it have three connections on it? Can you get CH WITHOUT HW coming on? There will be two pipes connected to side of the cylinder. Do either of these pipes have a contraption fitted with a thin wire going to a doofer clamped to the cylinder.
 
Its a 3 port valve, Yes CH comes on without HW or vice versa. However this morning i've noticed when on CH only there was hot water dripping from a overflow pipe (outside near roof edge which appears to be coming from roof tanks??) and it stopped as soon as i shut the CH down. Any ideas?

Here attached pic from airing cupboard.

//www.diynot.com/network/san04/albums/
[/img][/list]
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top