poty boiler fails to ignite,fan starts,aps proves,spark at burner,checked over heat stat ok,18v at gas valve,should be 210v+

So I here you say its the dreaded PCB?,
well I have changed the PCB for the 5111603 TWICE thinking the first was faulty,
Can I be that unlucky to have TWO faulty PCBs :cry:
 
Sponsored Links
What's your GV resistances? Should be 1400 & 2800.

SHort on GV used to take th eold board with it sometimes. Wonder if the new one does too :( :rolleyes:
 
yes ChrisR i,ve heard about the gas valve taken the older PCBs out.

I checked the voltage at the GV on black /red wires before I attached it to the GV.at the same time as spark

Should the resistance on the GV be 4000? :cry:
 
and who paid for the second pcb which you blew up ?

CORGIS ... always good for a laugh

... as long as you don't foot the bill
 
Sponsored Links
up yours

if you can''t properly diagnose a fault, keep away from boilers - clueless CORGIs are not only expensive, they're dangerous

... and you sound clueless to me - I only asked who paid for your incompetence
 