Powering gas combi from pure sinewave power generator
15 Oct 2007
Surrey
Hi, im currently looking at whether or not my viessmann 050w gas combi would run ok from a jackery explorer (eg 1000 v2 or similar) power station in the event of a power outage. Ive done some research and it seems the pure sinewave output is important but theres also something about checking earthing and flame detection. I can ask a pro but do i need an electrician or a heating engineer to confirm? I havnt purchased the powerstation at this point due to cost so seeing if theres any views here. Any comments welcome!
Yeah i fully expect that response from viessmann or any other main manufacturer, it wont answer the question though. Thanks
…but it is still worth trying IMO. What I was really trying to say was that asking a heating engineer or electrician is unlikely to get an accurate answer, unless by some chance they have direct experience. It’s not something they learn at college! More likely they’ll share the same anecdotal advice you could find online.
It might be worth asking the generator supplier how much the output varies from a pure sine wave. I could be wrong, but I can't see a reason it won't be as good a sine wave as a mains alternator in a power station. Might be better than from solar panels and wind farms, which use inverters.
Ok thanks, ill give them a try maybe ill get the detailed earthing config from jackery first, others must be considering the same, if it could work it would be a very handy way to keep the cold off during outages. I dont fancy another Christmas day without heating, like a few years ago!
I hope an inverter will work, as that is what I have, and 99% sure it will, my inverter on a power failure connects neutral to earth. I have no idea if they all do that?
I have over the years often found problems with generator earthing systems. And some were what seemed well known names, like Honda, were the output was 55 - 0 - 165 not 0 - 220 as expected.
Without actually testing, or detailed installation instructions, I have no idea if earthed at all, never mind if correct earthing for the spark igniter on a boiler, but really the boiler should not need the earth to be bonded to neutral to work anyway, as if it did, that could take the earth leakage over the edge and cause a RCD to trip.
If the generator/powerstation whatever else has the earth connected internally, then the boiler will work.
If the earth is not connected, the boiler will not work, and will show some error code.
That can be fixed by connecting the generator earth to the generator neutral.
Before doing that, it is essential to check that the generator earth and neutral are NOT connected in any way by checking for voltage between the earth and neutral output terminals / socket with it energised. A low impedance meter should be used to avoid any possibility of phantom readings.
No voltage = no connection, so they can be connected together.
If there is some voltage, then further investigations will be required.