I will need to take the xchanger off for a while as i need to descale it.
Do you? The lime scale forms on the secondary (domestic hot water side) of the plate heat exchanger, so you could leave it connected to the primary (boiler) side and connect a descaling pump to the 22mm secondary connections (disconnect the cold water feed and the hot water outlet) .
You can get obstructions on the primary side, but that would indicate sludge and a corrosion problem with the radiators through lack of corrosion inhibitors. That should not happen. The problem is most commonly with the secondary side.
PS the 3-way TMV on those is unreliable so |I'd suggest you ensure that it is working before getting into major bypass surgery on the plumbing.