I am new to this website (and to tinkering with a CH system) and have found the forum very informative. I have used what I have read to try and solve a problem we are having but would appreciate some feedback on what I have done to see if there are any other suggestions as to the root of the problem.
We have a Vokera Syntesi combination boiler and when the CH started coming on a week or so ago we noticed that the pressure was down at almost zero. I topped it up using the filling loop to 1 bar. I also checked all radiators and found no leaks.
When the heating came on, the pressure in the system rose to over 3 bar and the PRV started dripping. When the system cooled the pressure was back down to about 0.2 bar.
With the system cold, I located the expansion vessel and depressed the valve at the top. A small puff of air came out then stopped. No water came out. I used a pump to increase the air pressure to 1 bar. As I did this, the pressure in the CH system also rose to about 1bar. Was this supposed to happen?
Now when the heating comes on, the presssure still rises but now it goes from 1 bar to about 1.7 bar. Does this seem like a normal increase in pressure?
Overnight last night (and after the heating had been on this morning) the system pressure had dropped to about 0.3bar. It's raining at the moment so hard to tell but I think the PRV is dripping at a rate of about 1 drip every 3 mins. Could this have caused such a pressure drop? From what I have read, I understand that I probably need to replace the PRV. Is this correct?
My final question (I think) concerns the fact that we have done a lot of 'topping up' recently. From other posts I gather this means I should put some corrosion inhibitor into the system. How do I go about doing this?
Sorry to ask a lot of questions that may have been addressed elsewhere but as a complete newcomer to things like this I would really appreciate some confirmation that I have been doing the right things.
Thanks.
We have a Vokera Syntesi combination boiler and when the CH started coming on a week or so ago we noticed that the pressure was down at almost zero. I topped it up using the filling loop to 1 bar. I also checked all radiators and found no leaks.
When the heating came on, the pressure in the system rose to over 3 bar and the PRV started dripping. When the system cooled the pressure was back down to about 0.2 bar.
With the system cold, I located the expansion vessel and depressed the valve at the top. A small puff of air came out then stopped. No water came out. I used a pump to increase the air pressure to 1 bar. As I did this, the pressure in the CH system also rose to about 1bar. Was this supposed to happen?
Now when the heating comes on, the presssure still rises but now it goes from 1 bar to about 1.7 bar. Does this seem like a normal increase in pressure?
Overnight last night (and after the heating had been on this morning) the system pressure had dropped to about 0.3bar. It's raining at the moment so hard to tell but I think the PRV is dripping at a rate of about 1 drip every 3 mins. Could this have caused such a pressure drop? From what I have read, I understand that I probably need to replace the PRV. Is this correct?
My final question (I think) concerns the fact that we have done a lot of 'topping up' recently. From other posts I gather this means I should put some corrosion inhibitor into the system. How do I go about doing this?
Sorry to ask a lot of questions that may have been addressed elsewhere but as a complete newcomer to things like this I would really appreciate some confirmation that I have been doing the right things.
Thanks.