Has anyone got the Honeywell wiring booklet/guide? I downloaded it.

The wiring for a S PLAN with pump overrun doesn't make sense, the reason I say it is :

the boiler has a NEUTRAL and EARTH connection as normal, a PERMANENT LIVE to it, and still has the switched live from the ORANGE WIRES to it. The boiler provides LIVE to the PUMP via a separate terminal block. My point is: how does the pump run?

Pump overrun stats make when the temp is over 60 degrees C and open when the temp is under, so when the boiler 1st starts up, and the water is a lot lower, does the pump not run ??? .....
 
Sponsored Links
When the Boiler is Cold, the Pump is fired via the SwL terminal, it works like this,

Over heat Stat Common = Pump Live
Over heat stat Norm Open = Perm L
Over heat stat Norm Closed= Sw L

therefore when cold pump is fed by SwL, once hot feed transfers to Perm Live, untill boiler stops and cools down

Simples ;)
 
I see, so the switched live to the boiler, also feeds the pump as well, via the boiler....

A lot of newer modern boilers with internal pumps, like combi's, the pump is part of the firing sequence and controlled by the PCB isn't it.
 