Question
10 Oct 2013
Bristol
Hello all
I recently moved into new apartment where i have a biasi boiler yesterday i decided to try it and i turned on the heating the boiler started and the first two lights started flashing it was heating and the furnace was turning on and off but the pump was running constantly it is wired to an old thermostat which when i turn it off it doesnt turn off the boiler when i turn the button to on the boiler is still on but the 2nd light disappears and now the first and third are flashing is this ok?
1st and 3rd lights indicate a normal demand for CH when flashing together.
Flashing alternately and its a demand for hot water.
How does Bristol compare with the US ?
You have a different problem.
And I expect you only have one light visible.
actualy the first two lights are flashing together. I read a manual it says frost protection but nowhere is mentioned how to deal with it
That indication would indicate that a temperature sensor has a too high resistance. But it can also be a PCB fault!
If you want to start learning about boilers then leave it off for two hours and measure the resistance of each sensor.
Or may be easier to call a repairman?
About 13k at cooler room temp!
Measure with connector off of course.
Put connector on and off about five times as that cleans off any metal oxide which could be causing a higher resistance.
Sounds like you did not leave boiler off for two hours!!
2.7 K implies the boiler is at about 40 C and not cold.
Try again!
Test the calibration of the meter too.
The sensors would need to be closer to 20 K to provoke the frost stat operation.