Hi all
Quick question for you, sister inlaw has moved into a new flat
and it has a ravenheat rsf84e boiler, until last night it's been fine no problems, the heating is ok but she cant get any hot water only warm, when you run the water the boiler main burner lights :confused: is their a temp sensor at fault or a diverter valve not working
cheers
 
Sponsored Links
DHW Thermistor/NTC. Is the water running luke warm and then cold with burner coming on and off.
 
DHW Thermistor/NTC. Is the water running luke warm and then cold with burner coming on and off.

cheers for the quick reply,
the burner stays on all the time till the tap is turned off
 
Sponsored Links
Feel the heating pipes underneath the boiler. If the flow pipe is very hot it means your losing power to the radiators and inturn you water wont get as hot.

Is this likely to be a faulty diverter valve.
 
Feel the heating pipes underneath the boiler. If the flow pipe is very hot it means your losing power to the radiators and inturn you water wont get as hot.

Is this likely to be a faulty diverter valve.

Then its the potentiometer not regulating the gas valve.
__________________
cheers chaps will check it out tonight, would i be able to order the said parts online from ravenheat or a local trade center
 
I hope Craig remembers how this one works.

It might be a gas supply problem, thats less common but just to remind me I have been to two last Sunday!

But testing for that is a CORGI job but you could run the DHW and see how long it takes for one turn of the 1 cu ft dial on the meter.

Tony
 
I hope Craig remembers how this one works.

It might be a gas supply problem, thats less common but just to remind me I have been to two last Sunday!

But testing for that is a CORGI job but you could run the DHW and see how long it takes for one turn of the 1 cu ft dial on the meter.

Tony
Hi Tony I changed the meter & regulator when she moved in for it was fitted with a credit meter (work for scottish gas network) so the pressure sits fine at 21mb working pressure, not to say that the governors not went to fault :eek: another thing to check cheers Tony
 
Thinking purely from memory Tony, seem to remember the flow switch also regulates the gas valve.

Oh I envy you getting on that training day (ARGI).
So im lookin in the correct field, NTC,POT and flowswitch regulate the DHW :?:

;)
 
Could be worth checking the wp at the boiler when dhw is on max temp and max flow
 
found out if you reduce the flow through the taps the water heats up :!:
 
Thats only to be expected!

But there are only three likely reasons for the poor DHW:-

xxx Lack of enough gas to burner, usually supply problems.

xxx Temperature control fault.

xxx Lack of heat transfer from burnt gas to DHW.

Craig, this boiler is no longer in the mainstream so was not really covered in much detail as the current market is of course the condensing models.

Tony
 
hi i folks
thought i would give you an update with this boiler :cry:
we changed the potentimeter, & the dhw sensor, & its still the same, found out the flat above had a flood, and water was in the boiler, which we found out when we took the plastic pipe from the gas valve to the boiler case, had water in it, do you think this gas valve could be the problem? cheers
 
Until you or a competent CORGI measure the gas pressure at the inlet to the boiler and to the burners then we cannot advise you further.

Tony
 