Hi all Electrical section,
I have a problem with one of my ring mains - it keeps tripping the main RCD, I spent the whole of saturday narrowing it down to which one & I have now disconnected it from the consumer unit, as to get house up & running again.
The house has a conservatory & loft conversion & has 3 ring mains (done in 1999 as far as I can make out from the history of the property)
This is what I have done so far & it has had no effect:
1. Removed everything from the sockets on the faulty ring (I think!) including disconnecting some fused spurs
2. checked with a meter for shorts between phase & Earth & phase & Neutral - none
3. tried a different MCB
Alot of the sockets are in the conservatory it's very cold & damp in there at the moment - so could it be damp/water issue?
Could the RCD itself be faulty - obviously highly unlikely as the other 2 rings are fine - fully loaded, all high current devices - heaters/kettle/immersion etc working fine
some of the wiring in the house is a right mess! - wiring & spurs everywhere, especially in conservatory.
The other 2 rings are fine & the faulty ring does not trip the 32A MCB - only the main
never had a problem with it in 6 years - it's just happened overnight.
So I am looking for some fault finding advice - is it now just a case of removing each socket & inspecting the integrity & condition of the wiring?
I am a 20 year time served Electrical technician (just not domestic!) and can borrow any test equipment from work if needed.
Any advice welcome thanks in advance
I have a problem with one of my ring mains - it keeps tripping the main RCD, I spent the whole of saturday narrowing it down to which one & I have now disconnected it from the consumer unit, as to get house up & running again.
The house has a conservatory & loft conversion & has 3 ring mains (done in 1999 as far as I can make out from the history of the property)
This is what I have done so far & it has had no effect:
1. Removed everything from the sockets on the faulty ring (I think!) including disconnecting some fused spurs
2. checked with a meter for shorts between phase & Earth & phase & Neutral - none
3. tried a different MCB
Alot of the sockets are in the conservatory it's very cold & damp in there at the moment - so could it be damp/water issue?
Could the RCD itself be faulty - obviously highly unlikely as the other 2 rings are fine - fully loaded, all high current devices - heaters/kettle/immersion etc working fine
some of the wiring in the house is a right mess! - wiring & spurs everywhere, especially in conservatory.
The other 2 rings are fine & the faulty ring does not trip the 32A MCB - only the main
never had a problem with it in 6 years - it's just happened overnight.
So I am looking for some fault finding advice - is it now just a case of removing each socket & inspecting the integrity & condition of the wiring?
I am a 20 year time served Electrical technician (just not domestic!) and can borrow any test equipment from work if needed.
Any advice welcome thanks in advance