Would like some advice, before I finally section myself......
I've lived in house for 5 years and always had HW programmed morning and night, but CH on programmer set on Constant. I would then use stat to control temp along with TRVs.
Noticed in the past few days house has been a lot warmer than usual. Last night I clicked stat down from 21 to 18 and then went to check boiler - still running - where as before it would shut down. The only way to turn off the CH is to turn prog to off.
Having spent hours reading up, I am pretty sure I have a y plan system, 3 port valve.
The stat is a Honeywell T6360. I removed the two wires from 1 & 3, heating still ran, and I notice I have 240v on both cables. My understanding from reading is that when the programmer says CH on, then live is sent to one wire. The other wire is a switched live, so when stat is on it completes the circuit. So I'm confused as to why the switched live is live even when disconnected from stat.
I've followed guides on testing the valve, with power off, it defaults to HW, and moves to all 3 positions, but have read about microswitches failing - could this be a possible cause of the problem? It's a Tower MP322C/H, made by Grasslin dated 2003.
I'll be honest it's the first time I've looked into our heating system, and it is quite a learning curve for me. I'd like to check things as far as possible before calling an expert out to fix it!!
Any help much appreciated.....
I've lived in house for 5 years and always had HW programmed morning and night, but CH on programmer set on Constant. I would then use stat to control temp along with TRVs.
Noticed in the past few days house has been a lot warmer than usual. Last night I clicked stat down from 21 to 18 and then went to check boiler - still running - where as before it would shut down. The only way to turn off the CH is to turn prog to off.
Having spent hours reading up, I am pretty sure I have a y plan system, 3 port valve.
The stat is a Honeywell T6360. I removed the two wires from 1 & 3, heating still ran, and I notice I have 240v on both cables. My understanding from reading is that when the programmer says CH on, then live is sent to one wire. The other wire is a switched live, so when stat is on it completes the circuit. So I'm confused as to why the switched live is live even when disconnected from stat.
I've followed guides on testing the valve, with power off, it defaults to HW, and moves to all 3 positions, but have read about microswitches failing - could this be a possible cause of the problem? It's a Tower MP322C/H, made by Grasslin dated 2003.
I'll be honest it's the first time I've looked into our heating system, and it is quite a learning curve for me. I'd like to check things as far as possible before calling an expert out to fix it!!
Any help much appreciated.....