Siemens SSA61 0-10V radiator values

Discussion in 'Plumbing and Central Heating' started by slip.cougan, 1 Nov 2020.

  1. slip.cougan

    slip.cougan

    Joined:
    10 Dec 2015
    Messages:
    36
    Thanks Received:
    0
    Location:
    Kingston-upon-Hull
    Country:
    United Kingdom
    I've picked up about half a dozen of these to control my radiator valves.

    I'm modulating these with Crestron 0-10V controllers (DIN-4DIM-FLV4). Measuring the controller output these do indeed measure 0-10V exactly when modulating the valves but the valves do not operate.
    I'm using the supplied Siemens cable which is wired:
    Red - 24V
    Grey - 0-10V control
    Black - 0V

    I've tried running these on 24Vac & DC to no avail. Am I wasting my time with these?
    If so can anyone recommend a suitable replacement?

    The DIN-4DIM-FLV4 is actually a 4 channel 0-10V lighting controller but totally suitable for this purpose.

    Cheers
    -s
     
  2. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,020
    Thanks Received:
    2,471
    Location:
    Bedfordshire
    Country:
    United Kingdom
  3. Sponsored Links
  4. slip.cougan

    slip.cougan

    Joined:
    10 Dec 2015
    Messages:
    36
    Thanks Received:
    0
    Location:
    Kingston-upon-Hull
    Country:
    United Kingdom
    Apologies for the late reply on this topic. Work has dictated that I don't get to do fun stuff right now.

    Anyway an update:
    I picked up a Ballorex APR-40405 (0-10V wax proportional actuator) as a test.
    This works as expected (apart from the fact the control is inverted - an easy fix in programming)
    So it certainly looks like none of the Siemens SSA's work. These were all brand new units out of the box so I simply don't understand why are not playing ball.
    What's more, they are supposed to run an auto calibration on power-up - they don't. They all move to pretty much the same 50% position and stop.
    Doesn't matter if they have a control voltage applied or not.

    @bernardgreen,
    Thanks for responding.
    I checked all the specs before I bought these and the run time of 34 seconds is actually pretty quick compared to a wax based actuator. This is why I went for motorised. I've certainly waited long enough for them to position. Also being motorised I should be able to adjust the voltage and see them move instantly as they have a positional indicator on the top.

    Cheers
    -s
     
  5. slip.cougan

    slip.cougan

    Joined:
    10 Dec 2015
    Messages:
    36
    Thanks Received:
    0
    Location:
    Kingston-upon-Hull
    Country:
    United Kingdom
    So Basically I'm a complete dumbass.
    The SSA61's need to be fitted to the valve. Then once powered up they run the calibration.
    Once calibrated they work as they should.
    Lesson learned :)
    -s
     
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page