what are the implications of using a 3 phase generator to deliver a single phase load?
ie, just using one of the phases.
ie, just using one of the phases.


That's interesting, we were once provided with a 12KVA to run a sound stage. Our rig was ~6KW and single phase on 32/1, ie in we weren't set up for 3ph, no way could it run a 6KW rig, the voltage just dropped off to the point the amplifiers dropped out and took seconds to self test and start TBH it struggled with 3KW with the varying load.Sunray's interpretation of the kVA rating differs from mine. I worked installing and testing diesel generators for 10 years and in my experience, a 10kVA generator will be able to supply 10kVA per phase.
Obviously I'm not taking power factor into consideration and I'm a user of such devices not a provider so I don't have the same detailed knowledge.When calculating the test current, we applied 0,8 power factor to the kVA so a 10kVA would be able to supply 8kW. With a little maths involving root 3 it gives a rule of thumb of 1.4 amps per kW so a 10kVA set should be fine for 11.2 amps per phase.
Loading one phase should be avoided in an ideal world as it tries to raise the neutral voltage above earth potential. In reality, it doesn't cause any long term damage. Just make sure you have adequately sized earth conductors.

I'm personally not aware of it being anything else but as I said the nitty gritty of this has not been my bag.I would also consider 12 kW to be 4 kW per phase.


Inverters be they static or rotary have been used for years, who remembers the Lincoln welding sets. Be them electric or diesel powered?A three phase motor, a fly wheel and a single phase generator is an option.
Sunray's interpretation of the kVA rating differs from mine. I worked installing and testing diesel generators for 10 years and in my experience, a 10kVA generator will be able to supply 10kVA per phase.
I would also consider 12 kW to be 4 kW per phase.
Having had a very quick look around, I suspect that marketing people are inconsistent in their 'top-line'descriptions - such that a 3-phase generator capable of delivering 4 kW per phase may be described as either "4 kW" or "12 kW". However, if one looks at the actual spec., one discovers 'the truth'I'm personally not aware of it being anything else but as I said the nitty gritty of this has not been my bag.

Sunray's interpretation of the kVA rating differs from mine. I worked installing and testing diesel generators for 10 years and in my experience, a 10kVA generator will be able to supply 10kVA per phase. When calculating the test current, we applied 0,8 power factor to the kVA so a 10kVA would be able to supply 8kW. With a little maths involving root 3 it gives a rule of thumb of 1.4 amps per kW so a 10kVA set should be fine for 11.2 amps per phase.
Quite so. I don't think it's you who is missing anythingAt the end you conclude with "11.2 A per phase", which (at 240 V) is 2688 VA. Three of those is 2688 x 3 = 8 kVA, which is kinda 10 kVA allowing for your 0.8 power factor. So that's 10 kVA *total*, not 10 kVA *per phase*. But you say "a 10kVA generator will be able to supply 10kVA per phase". What have I missed?

Is not ideal, but it does seem to work. The generators actually had 12 coils, allowing 400 volt three-phase, 230 volt single phase and 110 volt centre tapped. And were designed to be configured to give variable outputs.If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.