my mother has a large indoor fitted spa which has a 6kw heater inline. the water content is 600 gallons. The water no longer seems to heat up much like it used to do, it used to take about 72 hours to get to 40 degrees. now even after 7 days it only reaches 25 degrees. i have tested it all electrically and everything is fine. there is 230 volts at the heater terminals and each element has 31 ohms resistance. if i frig the control circuit so the water stops flowing but the heater stays on, the heater tube gets red hot and the water boils. so therefore electrically it is fine.
any ideas as to what could be preventing the heating? i thought maybe the tube was airlocked but it appears not to be as i have bled any air out. there is also adequate flow through the heater.
i have not posted in electrics as i feel its not an electrical problem anymore.