can you wire a spur from a spur from a spur?

can you wire more than one spur from a single double socket, ie, two spurs directly from a single double socket?
 
Sponsored Links
Assuming that all the spurs are protected by an appropriate fuse, can you justify that?
 
The reason for the questions is basically this - I have been asked to wire a garage which stands separately from the house. The client does not want to me to put in a new consumer unit and feed it from the unit used for the house - the garage is quite some distance way from the house and would be a real pain in the arse to get too. A separate power supply is also out of the question.

The garage replaces an existing one which basically had two sockets, and a 5a spur spur for the lighting. These were fed as a chain of spurs from a double socket in the ground floor ring of the house - ie, a single leg from the socket was fed out to the garage through pvc conduit under the lawn.

I have a feeling that this is not ideal, but have been told i can get away with this is if i do it for the new garage as well. The new garage requires two double sockets, a single socket for the electric door, a 13a fcu for a fountain in the garden, an a 5a fcu for the lighting. The idea is to spur them from one another in a sort of radial from the house ring.

Any suggestions?
 
Sponsored Links
spur off the socket, into a fused spur(13amp fuse), out to the garage, that way its a sub circuit, not a spur


AR
 
supersparks said:
spur off the socket, into a fused spur(13amp fuse), out to the garage, that way its a sub circuit, not a spur


AR

Couldn't agree more....and the garage is protected by the 13A fuse....
 
supersparks said:
spur off the socket, into a fused spur(13amp fuse), out to the garage, that way its a sub circuit, not a spur


AR



In this case i am assuming that the arrangement in the garage can now be treated as radial sub-circuit.

Can the sub-circuit be made into a ring, so that it originates and ends at the 13amp fused spur?
 
In this case i am assuming that the arrangement in the garage can now be treated as radial sub-circuit.

Can the sub-circuit be made into a ring, so that it originates and ends at the 13amp fused spur?[/quote]

Yes pretty much, trat as a radial, but why would you want to turn it into a ring? you would only gain more hard work./......

AR
 
I agree! It was just a hypothetical question.

Is there any maximum to the number of sub-circuits you can have originating from a ring?
 
got your back ban.........go head let him av' it :evil:
 