Supply characteristics
27 Sep 2006
Yorkshire
Here is a question regarding the supply to a normal household.
The CU is wired in TN-S (as the earth is separated from the neutral bar), but back at the Elec Boards transformer - would I be correct in saying that the Neutral is connected to Earth (therefore TN-C-S)?
With that in mind, when the Installation Cert is signed up, do you enter supply characteristics as TN-S (as found at the house CU) or do you enter TN-C-S (as this is technically the supply from the E board) ?
Seeing as most sparks don't have access to the other end of the cable, you can only record what shows at the consumer's end of the cable.
Or maybe TT, as back at the transformer, not only are N & E linked, they are also connected to an earth rod... :wink:
Earthing arrangements such as TT, TN-S, TN-C-S etc are not derived from what happens at the tranny end of the supply.
It all depends on the service head.
A seperate earth from the tranny to head, weather a seperate cable, an extra core in a cable, a cable sheath etc will be TN-S
If the earth is derived from the neutral AT THE HEAD, it will be TN-C-S
In our area, we have split concentric cables at the head - seperate N and E. Therefore TN-S. HOWEVER, these cables go out to the street and joint in feeder pillars - these are basically unfused joint boxes. These pillars are fed with a 3 core 185mm waveform concentric cable, therefore being TN-C-S. The recorded earthing type is still TN-S according to the DNO and NIC.