System losing pressure

Joined
12 Oct 2013
Messages
106
Reaction score
0
Location
Norfolk
Country
United Kingdom
Hi all,

I have a closed central heating system and the pipes to and from the radiators are run between the joists (upstairs) and under the screed (downstairs).

The system usually runs at a pressure of 1 bar, but over the course of a couple of weeks, the pressure in the system slowly declines to zero.

I assume there must be a leak somewhere, but I cant see any signs of it. If the upstairs pipes were leaking, surely there would be damp patches on my downstairs ceiling? If the downstairs pipes were leaking, wouldn't it show on the screed? I currently have bare screed and some of the rooms are tiled downstairs.

Is there a smart way I can find out what's causing the loss in pressure?

Thanks in advance for any help.

Jever
 
Sponsored Links
Go outside... there will be a small copper pipe sticking out of the wall from behind the boiler - it usually points back towards the wall... sort of like an inverted U shape

Any water coming out of there?
 
Be aware that it could also be a holed hex and system water escaping down condensate drain. :notworthy:
 
Or expansion vessel issue... but, the water’s going somewhere...
 
Sponsored Links
Hi,

The boiler is oil fired from the eighties. I've been outside, there are no pipes poking out of the wall. If I look behind the boiler, there's a pipe to and from, but nothing that would vent into a waste system.

I had the closed system with a tank installed a couple of years ago. The plumber that did it put in a vent next to the tank (see photo attached), but I never see anything dripping there.

Regards

Jever
 

Attachments

  • P1040664.JPG
    P1040664.JPG
    136.2 KB · Views: 129
Hi,

The boiler is oil fired from the eighties. I've been outside, there are no pipes poking out of the wall. If I look behind the boiler, there's a pipe to and from, but nothing that would vent into a waste system.

I had the closed system with a tank installed a couple of years ago. The plumber that did it put in a vent next to the tank (see photo attached), but I never see anything dripping there.

Regards

Jever

Well it would have helped if you'd posted that in the first place :rolleyes:
If the heating system is sealed then you will have a discharge pipe somewhere... Look for the expansion vessel and around that for PRV (plastic red top maybe) and discharge could go from that.

Boiler and other components make and model and location of everything please...
 
Hi,

The boiler is a Myson Velaire, located downstairs. I think I've found the PRV(s) - see photos attached. The tank and everything else I've given photos of are upstairs in the bathroom.

Items in these to photos are attached directly to the outlet I attached in the previous post.

I never see any water flowing through the outlet, but I guess that doesn't necessarily mean it isn't going out that way.

I assume the thing to do is to try to find a way to collect whatever might be flowing through the outlet?

Jever
 

Attachments

  • P1040665.JPG
    P1040665.JPG
    241.9 KB · Views: 98
  • P1040666.JPG
    P1040666.JPG
    225.4 KB · Views: 104

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top