Hi all,
This is a first long post but please read on.
First of all we have had major building work at the house due to storm damage in November 2009. We are still living in temporary accomodation and not living at the property until everything is repaired and our furniture is returned from storage.
We have a Worcester Bosch 35CDi II installed in September 2006 by the previous owner. It is a 2 storey house with the boiler located downstairs.
We have Scottish Gas HomeCare 400.
In February 2010 underneath the boiler there was a cold water drip leak coming from a big compression joint. A plumber tightened it up and the boiler ran fine with no visible leaks. No pressure loss was noted.
Another plumber said later that it is part of the diverter valve.
We had a mixture of old copper pipework downstairs, a bit of plastic pipework in the kitchen and microbore upstairs.
The builders found that the upstairs tail pipe ends were leaking so the system was switched off and drained down in March 2010 and not repiped until October 2010.
The system was recommissioned with Hep2O barrier pipe upstairs, 4 new radiators (because the builders lost the old radiator brackets), new lockshields and new TRVs on 13th November 2010.
The boiler was given an initial inspection by Scottish Gas on 19th November 2010. He checked the expansion vessel, electrical safety, gas emmision at the flue etc. All OK. The system ran fine for 1 week at 1.5 bar.
On Friday 26th November 2010 the pressure was noted to be 2.2 bar which I thought was too high but I thought maybe the builder had topped it up after bleeding one or more of the radiators. I remember this because it started snowing outside and it was really cold outside.
On Saturday 27th November 2010 the pressure was at 0.8 bar which I know was too low. I contacted the builder who advised how to top it up using the filling loop key\grey button to 1.5 bar. The boiler lost pressure every day thereafter.
In general the system pressure went down from 1.5 bar to 0.8 while running continously for 12 hours. It lost more pressure when it was switched off and cold.
Scottish Gas visit 1: 1/12/2010
The engineer checked the charge on the expansion vessel. It was "a bit low". It was topped up expansion vessel to 1 bar. The system was repressurised to 1 bar cold.
Replaced PRV.
The system drain pipe was inspected and a big icicle from the PRV drain pipe suggested that the PRV was passing water and\or stuck open.
The system still kept losing pressure.
Scottish Gas visit 2: 2/12/2010
The engineer tightened a few compression joints on the boiler. He check the Schrader Valve and expansion vessel pressure again (both were OK)
and looked under the floor boards upstairs but found nothing.
Scottish Gas visit 3: 3/12/2010
The engineer ran a boiler isolation test. The boiler was isolated for 7 hours, then he came back. The pressure dropped in seconds after being reopened. This showed that there is likely to be a leak on the system, not the boiler. He didn't have any leak sealant and his boss didn't like using it on "leaks of this size", so he left and asked me to book another
appointment when he would come out with some leak sealant.
Scottish Gas visit 4: 8/12/2010
The engineer ran Salamander leak sealant through the system. No change.
Scottish Gas visit 5: 14/12/2010
The engineer inspected under the floors downstairs but no leak was found.
Scottish Gas then gave me a quote for repiping downstairs.
They said it would take 3\4 visits to cut and cap downstairs into zones to test each bit individually but I couldn't take the time off work for all that.
The system pressure held at 1.5 bar for 5 days 23-27th December. Maybe the leak sealant worked for a while.
I bled one cold radiator upstairs and topped up the boiler again.
The pressure loss came back.
Scottsh Gas then have me a quote for a downstairs repipe but then said they couldn't do it until the end of January\start of February
because all the engineers in the area are working on maintenance, not upgrades! They advised that I could get a local company
to repipe downstairs. It wouldn't break the HomeCare agreement "if it was done properly". I got a couple of quotes and went
with a big local company who could come in at the start of January.
We were repiped in copper downstairs on 10/1/2011 and they got rid of a lot of mess e.g. pipes running up the corridor then back down to a radiator and bits of Hep2O in the kitchen. They worked well and the system doesn't creak when warming up now.
- They didn't repipe a bit in the bathroom to prevent lifting tiles.
- They found a leak in the small living room at a corner joint literally 2 feet away from where Scottish Gas looked.
- They fitted all new pipework and lagging, new TRVs, new lockshields and ran a cleanser and inhibitor through the system.
- They ran a pressure test at 3.2 bar for 1 hour with no problems then lowered the pressure to 1.5
The pressure dropped to 0.8 within 4 hours of them leaving.
The system is now losing pressure down from 1.5 bar (hot) to 0.3 bar every 8 hours so I top up and run the boiler from 7:30pm - 11pm and
8:30am - 9:30am to keep the house warm when I come home and before I go to work.
The heating engineers came back on 17/1/2011 and lifted the tiles in the bathroom to check there, they inspected every pipe and every joint they fitted downstairs and found no leaks on the pipework when running (hot) and when the system was switched off (cooling down).
My questions are:
The boiler or system still loses pressure when filled to 1 bar cold and the heating is left off.
Where does the water go? Does it fill the pipes downstairs?
I don't know about plumbing but surely it can't go upstairs without the pump running?
I have noticed drips below the boiler but it is not coming from the big compression joint tightened in February 2010. It doesn't seem to be coming from the filling loop key area because I dry the little basin I put below it every time I fill it. It is more than a couple of drips you get by removing the filling key, maybe 20-30ml of water.
I have several worries:
1. There is a leak upstairs requiring laminate flooring to be lifted,
2. It is in the pipe chase that goes upstairs,
That is the only bit of original pipework left in the house but there are no drips at the bottom of the pipe chase.
3. Could it be the central heating drain pipe?
It worked properly when the system was drained down for downstairs repiping and the Scottish Gas engineers couldn't see of feel
any drips there.
For the amount of water the system is losing if the leak was upstairs we'd have seen it on the ceilings by now.
I have now called Scottish Gas back to perform another isolation test and\or a full service of the boiler.
Please advise! I'm at the end of my tether and this is keeping us out of our house! We can't get new carpets and our furniture delivered until this is sorted out and the heating engineers and builders are gone.
This is a first long post but please read on.
First of all we have had major building work at the house due to storm damage in November 2009. We are still living in temporary accomodation and not living at the property until everything is repaired and our furniture is returned from storage.
We have a Worcester Bosch 35CDi II installed in September 2006 by the previous owner. It is a 2 storey house with the boiler located downstairs.
We have Scottish Gas HomeCare 400.
In February 2010 underneath the boiler there was a cold water drip leak coming from a big compression joint. A plumber tightened it up and the boiler ran fine with no visible leaks. No pressure loss was noted.
Another plumber said later that it is part of the diverter valve.
We had a mixture of old copper pipework downstairs, a bit of plastic pipework in the kitchen and microbore upstairs.
The builders found that the upstairs tail pipe ends were leaking so the system was switched off and drained down in March 2010 and not repiped until October 2010.
The system was recommissioned with Hep2O barrier pipe upstairs, 4 new radiators (because the builders lost the old radiator brackets), new lockshields and new TRVs on 13th November 2010.
The boiler was given an initial inspection by Scottish Gas on 19th November 2010. He checked the expansion vessel, electrical safety, gas emmision at the flue etc. All OK. The system ran fine for 1 week at 1.5 bar.
On Friday 26th November 2010 the pressure was noted to be 2.2 bar which I thought was too high but I thought maybe the builder had topped it up after bleeding one or more of the radiators. I remember this because it started snowing outside and it was really cold outside.
On Saturday 27th November 2010 the pressure was at 0.8 bar which I know was too low. I contacted the builder who advised how to top it up using the filling loop key\grey button to 1.5 bar. The boiler lost pressure every day thereafter.
In general the system pressure went down from 1.5 bar to 0.8 while running continously for 12 hours. It lost more pressure when it was switched off and cold.
Scottish Gas visit 1: 1/12/2010
The engineer checked the charge on the expansion vessel. It was "a bit low". It was topped up expansion vessel to 1 bar. The system was repressurised to 1 bar cold.
Replaced PRV.
The system drain pipe was inspected and a big icicle from the PRV drain pipe suggested that the PRV was passing water and\or stuck open.
The system still kept losing pressure.
Scottish Gas visit 2: 2/12/2010
The engineer tightened a few compression joints on the boiler. He check the Schrader Valve and expansion vessel pressure again (both were OK)
and looked under the floor boards upstairs but found nothing.
Scottish Gas visit 3: 3/12/2010
The engineer ran a boiler isolation test. The boiler was isolated for 7 hours, then he came back. The pressure dropped in seconds after being reopened. This showed that there is likely to be a leak on the system, not the boiler. He didn't have any leak sealant and his boss didn't like using it on "leaks of this size", so he left and asked me to book another
appointment when he would come out with some leak sealant.
Scottish Gas visit 4: 8/12/2010
The engineer ran Salamander leak sealant through the system. No change.
Scottish Gas visit 5: 14/12/2010
The engineer inspected under the floors downstairs but no leak was found.
Scottish Gas then gave me a quote for repiping downstairs.
They said it would take 3\4 visits to cut and cap downstairs into zones to test each bit individually but I couldn't take the time off work for all that.
The system pressure held at 1.5 bar for 5 days 23-27th December. Maybe the leak sealant worked for a while.
I bled one cold radiator upstairs and topped up the boiler again.
The pressure loss came back.
Scottsh Gas then have me a quote for a downstairs repipe but then said they couldn't do it until the end of January\start of February
because all the engineers in the area are working on maintenance, not upgrades! They advised that I could get a local company
to repipe downstairs. It wouldn't break the HomeCare agreement "if it was done properly". I got a couple of quotes and went
with a big local company who could come in at the start of January.
We were repiped in copper downstairs on 10/1/2011 and they got rid of a lot of mess e.g. pipes running up the corridor then back down to a radiator and bits of Hep2O in the kitchen. They worked well and the system doesn't creak when warming up now.
- They didn't repipe a bit in the bathroom to prevent lifting tiles.
- They found a leak in the small living room at a corner joint literally 2 feet away from where Scottish Gas looked.
- They fitted all new pipework and lagging, new TRVs, new lockshields and ran a cleanser and inhibitor through the system.
- They ran a pressure test at 3.2 bar for 1 hour with no problems then lowered the pressure to 1.5
The pressure dropped to 0.8 within 4 hours of them leaving.
The system is now losing pressure down from 1.5 bar (hot) to 0.3 bar every 8 hours so I top up and run the boiler from 7:30pm - 11pm and
8:30am - 9:30am to keep the house warm when I come home and before I go to work.
The heating engineers came back on 17/1/2011 and lifted the tiles in the bathroom to check there, they inspected every pipe and every joint they fitted downstairs and found no leaks on the pipework when running (hot) and when the system was switched off (cooling down).
My questions are:
The boiler or system still loses pressure when filled to 1 bar cold and the heating is left off.
Where does the water go? Does it fill the pipes downstairs?
I don't know about plumbing but surely it can't go upstairs without the pump running?
I have noticed drips below the boiler but it is not coming from the big compression joint tightened in February 2010. It doesn't seem to be coming from the filling loop key area because I dry the little basin I put below it every time I fill it. It is more than a couple of drips you get by removing the filling key, maybe 20-30ml of water.
I have several worries:
1. There is a leak upstairs requiring laminate flooring to be lifted,
2. It is in the pipe chase that goes upstairs,
That is the only bit of original pipework left in the house but there are no drips at the bottom of the pipe chase.
3. Could it be the central heating drain pipe?
It worked properly when the system was drained down for downstairs repiping and the Scottish Gas engineers couldn't see of feel
any drips there.
For the amount of water the system is losing if the leak was upstairs we'd have seen it on the ceilings by now.
I have now called Scottish Gas back to perform another isolation test and\or a full service of the boiler.
Please advise! I'm at the end of my tether and this is keeping us out of our house! We can't get new carpets and our furniture delivered until this is sorted out and the heating engineers and builders are gone.